Minimum MCB of an electrical panel

Status
Not open for further replies.

zam

Member
Location
New York, NY
Regardless of how small the load is on the panel, does the NEC mention a minimum allowed size for the main circuit breaker of an electrical panel? Thank you.
 
Well, since MLO panels are commonplace, I'd have to say zero... :D

Even when a service panelboard is the item of issue, the NEC only specifies the minimum equipment rating, not the main circuit breaker rating. That is determined by the calculated load.
 
That is a little like asking if it is permissible protect a conductor usually rated for 100 amps with a 15 amp overcurrent device (or even less).

One difference is the conductor could have adjustments applied to it in some circumstances and have it's ampacity reduced - but panelboards don't get ampacity adjustments that I am aware of.
 