I don't know of anyone offering less than 600A main bus. As Bob said, there would be very little difference in cost anyway, but the other issue would be that the minimum vertical bus will be 300A, so a 200A main bus would be pointless.
If you need the convenience of an MCC in terms of removing buckets or isolating only one unit (because in a control panel, that's more difficult in light of the new Arc Flash issues), just get whatever is standard. But if the nature of your machine/process is such that if any one thing is off, they might as well all be off, then go with a control panel. You can get bus bar systems for use in control panels that allow you to unplug individual IEC style starters, any decent panel builder can do that for you and likely cost less than an MCC.