I realize that different wire will have different specification, but I have sort of a general question.
I was on a job yesterday that had a bathtub overflow for several hours. Our job was to determine if it would be safe to turn the power back on to the areas that got wet. After opening up fixtures, looking in the drywall where the plumber opened etc., I meggered the wiring. The home run to the bathroom was great +2,000 Megs. Some of the jumpers from plug to plug were what I would normally find acceptable at over 100 Megs. Two of the jumpers were only 2 megs. The interesting thing is that if we disconnect everything and check each jumper individually, we get over 100 megs on each jumper. Once we connect them together, it drops down to 2 megs or so. I would normally say this indicates a leakage at the wire nuts but the wires are sticking out of the box and are a good 6 inches from the box. (FYI, I'm talking hot to ground measurement)
OK, so even with 2 megs of resistance, it's not going to trip a breaker,and I don't think it is likely to pose a safety issue, but I need to understand what's is going on here before I power it up. This particular job is 12/2 MC cable with steel boxes.
Thanks
I was on a job yesterday that had a bathtub overflow for several hours. Our job was to determine if it would be safe to turn the power back on to the areas that got wet. After opening up fixtures, looking in the drywall where the plumber opened etc., I meggered the wiring. The home run to the bathroom was great +2,000 Megs. Some of the jumpers from plug to plug were what I would normally find acceptable at over 100 Megs. Two of the jumpers were only 2 megs. The interesting thing is that if we disconnect everything and check each jumper individually, we get over 100 megs on each jumper. Once we connect them together, it drops down to 2 megs or so. I would normally say this indicates a leakage at the wire nuts but the wires are sticking out of the box and are a good 6 inches from the box. (FYI, I'm talking hot to ground measurement)
OK, so even with 2 megs of resistance, it's not going to trip a breaker,and I don't think it is likely to pose a safety issue, but I need to understand what's is going on here before I power it up. This particular job is 12/2 MC cable with steel boxes.
Thanks