Minimum Neutral Size

Status
Not open for further replies.

lauraj

Senior Member
Location
Portland, Oregon
This is a theoretical question and I can't find any reference in the NEC for this.

112.5KVA, 480-208/120V xfmr feeding a panel with a 300A main breaker with 350kcmil conductors. System bonding jumper is located in the transformer.

If a grounded conductor is pulled, what is the smallest size it could be?

I say we must use T250.102(C)(1) and it would be a #2 CU, because if we had a line to neutral fault at the panel, it would need to be big enough to carry that fault current. But I sure can't find anything that tells me I need to use that table. 250.30(A)(2) which give minimum neutral conductor requirements for SDSs only applies if the system bonding jumper is not located at the transformer.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The code does not appear to address that installation. However I agree that it should be sized per the table you cited.
The feeder minimum size rule in 215.2(A)(2) does not apply because that is based on the size of the upstream OCPD, and there really isn't one in this application.
Might be a good place for a PI to make a change for the 2026 code.
 