Twoskinsoneman
Senior Member
- Location
- West Virginia, USA NEC: 2020
- Occupation
- Facility Senior Electrician
I'm calculating a service for a non-dwelling one room unit with lots of electronic equipment in it. Anyway 95% of the entire load well be single phase 240vac. I am trying to calculate the neutral wire. With the unbalcanced load being so small I came up with 6160VA. This includes mostly plug-in equipment with a few other receptacle outlets. This includes 140% increase. Do I really size the neutral for this or is there some minimun size?
Thanks this type of sizing-service-conductors by load is kinda new to me.
Thanks this type of sizing-service-conductors by load is kinda new to me.