Is there something in the NEC that addresses whether there is a minimum number of receptacles and spacing in a new Industrial building to be used for warehouse and production as there is for residential??
Not dedicated receptacles but convenience.
Each 15-20 A 125V receptacle counts at 180VA for a load calculation. The only required recp I am aware of would be for the electrical service area, which is new in the 2014 NEC.