manuel bonilla
Member
- Location
- San Jose, Costa Rica
What is the minimum operating voltage that an HVAC unit should operate with if it is built for a 208V system?
On a recent installation I found an equipment that says Min Voltage is 198V (4.8% under 208!!).
In this case, distribution voltage in the area is not very stable and tends to lower to 205V at the pad mounted transformer terminals (this an apartment building with a 120/208V Tx). Under this circumstances, considering 5% voltage drop to HVAC equipment terminals, voltage at that point would drop to 194V and it in fact triggers the HVAC protection.
Is not it true that the standard min. voltage for an equipment should be 10% under rated voltage?
On a recent installation I found an equipment that says Min Voltage is 198V (4.8% under 208!!).
In this case, distribution voltage in the area is not very stable and tends to lower to 205V at the pad mounted transformer terminals (this an apartment building with a 120/208V Tx). Under this circumstances, considering 5% voltage drop to HVAC equipment terminals, voltage at that point would drop to 194V and it in fact triggers the HVAC protection.