Hello all, I would like your opinion on the following: Consider an existing commercial building that is undergoing an extensive remodel - practically all of the existing electrical installations are to be removed and new to be installed. The intent, however, is for the existing 120/240V, 1PH service to remain. Tabulating the building's electrical loads per article 220 III, IV & V yields 450A.
The existing service entrance conductors are 3#750MCM copper THWN (good for 475A per table 310.15 of the 2014 NEC).
The existing main circuit breaker is a 2P-400A, 80% rated circuit breaker in an i-line distribution panel - this is where I'm a bit confused.
My conductors can handle my load, so I'm ok per NEC 230.42 and NEC230.90(A) only sets a MAXIMUM of the OCP on a service.
I do see that NEC 210.20 sets a minimum for OCP on branch circuits and NEC 215.3 sets a minimum for OCP on feeders, but I don't see anything that forces my OCP on my service to have a minimum rating. Thoughts?
The existing service entrance conductors are 3#750MCM copper THWN (good for 475A per table 310.15 of the 2014 NEC).
The existing main circuit breaker is a 2P-400A, 80% rated circuit breaker in an i-line distribution panel - this is where I'm a bit confused.
My conductors can handle my load, so I'm ok per NEC 230.42 and NEC230.90(A) only sets a MAXIMUM of the OCP on a service.
I do see that NEC 210.20 sets a minimum for OCP on branch circuits and NEC 215.3 sets a minimum for OCP on feeders, but I don't see anything that forces my OCP on my service to have a minimum rating. Thoughts?