We set a sub panel on a job for a client that had very specific ideas where he wanted it. It was a reasonably suitable space in the hall that would be behind a decorative door, the problem (or potential problem) was that it was only about 28" off the floor to the bottom of the panel. While not my 1st choice, I reviewed 110.26 and didn't see a problem from a code point of view. The inspector today said that while there isn't a minimum height for the panel, there is a minimum height for the breakers of 36" to the center of the handle. he referenced 240.24. However when I read 240.24 it does not give a minimum height, it states "Overcurrent devices shall be readily accessible unless one of the following applies:" I am looking at the 2002 NEC, did it perhaps change in 2005?
Also, I know there is a minimum working height exception for residential remodel, if there is in fact a minimum heigh can someone reference a code section so I can see if there is an exception.