Hi,
Has anyone run into a situation where the Equipment Grounding Conductor size based on NEC 250.122 gives a size larger than the phase conductor? I have a single phase 1.5HP motor at 208V supply. The motor table 430.248 gives FLC of 11A. I am using #12 awg phase conductors. My circuit breaker setting would be 30A per 430.52. Based on 250.122, the minimum EGC I need is #10.
I don't usually see EGC larger than phase conductor so I would like to know if there is anything I missed or exceptions that allows a lower EGC?
Has anyone run into a situation where the Equipment Grounding Conductor size based on NEC 250.122 gives a size larger than the phase conductor? I have a single phase 1.5HP motor at 208V supply. The motor table 430.248 gives FLC of 11A. I am using #12 awg phase conductors. My circuit breaker setting would be 30A per 430.52. Based on 250.122, the minimum EGC I need is #10.