Yes but 230.79 does say that the disconnect feeding these "sub panels" will but no less than 60 amps and since the disconnect is also your service OCPD (230.90/91) it will also be at 60 amps 408.16 will require the panel board to be rated at least 60 amps.They may not be service panels and if they're not then 230.79 doesn't apply.
Then you would have to follow 240.21(B)(1)By Mc5w If a metering center has a service switch and overcurrent protection ahead of the meters then the meter and line for each apartment is a feeder which does not need to meet a 60 amp or 100 amp minimum like with a service as far as NEC is concerned.