I have a calculated load of 187A for a tenant infill in a space with a 4/0 SER cable as the service entrance conductors.
I have done a few back flips to keep the load under 200A so we dont have to upgrade the service.
Now however the rating of the 4/0 SER cable 75C we all know is 180A
From the way I read this I am not allowed to use 240.4(B) "next size up" rule to calculate the ampacity of the minimum size service entrance conductor.
It appears to state that the wire at minimum shall have an ampacity of the calculated load.
Hopefully I am wrong
Or do I need another cup of coffee.
Thanks In advance
I have done a few back flips to keep the load under 200A so we dont have to upgrade the service.
Now however the rating of the 4/0 SER cable 75C we all know is 180A
From the way I read this I am not allowed to use 240.4(B) "next size up" rule to calculate the ampacity of the minimum size service entrance conductor.
National Electrical Code (C)NFPA said:230.42 Minimum Size and Rating
(A) General. The ampacity of the service-entrance con-
ductors before the application of any adjustment or correc-
tion factors shall not be less than either 230.42(A)(1) or (A)
(2). Loads shall be determined in accordance with Part III,
IV, or V of Article 220, as applicable. Ampacity shall be de-
termined from 310.15. The maximum allowable current of
busways shall be that value for which the busway has been
listed or labeled.
(1)The sum of the noncontinuous loads plus 125 percent of
continuous loads
Exception: Grounded conductors that are not connected to
an overcurrent device shall be permitted to be sized at 100
percent of the continuous and noncontinuous load.
It appears to state that the wire at minimum shall have an ampacity of the calculated load.
Hopefully I am wrong
Or do I need another cup of coffee.
Thanks In advance