I have giving up looking for the answer, does anyone know what the minimum size branch ckt size is for a commercial building feeding a 120 volt recpt? I thought is was #12 whether it was on a 15 or 20 amp breaker. (Let's assume we are using THHN)
 
I have giving up looking for the answer, does anyone know what the minimum size branch ckt size is for a commercial building feeding a 120 volt recpt? I thought is was #12 whether it was on a 15 or 20 amp breaker. (Let's assume we are using THHN)

For anything under 2000 volts a 14 copper or 12 aluminum, see Table 310.5 Minimum Size of Conductors
 