I have a commercial client just had installed a new FACP 250' from the only distrib.
760.121(B) says I need a dedicated circuit.
The path is 3/4" rigid in concrete slab w [4] #12s. (Phase Phase Grounded Grounding)
The wires move. I think I could pull in a new pair if I have to.
My question:
The PLFA ct has a negligible load.
Can I take the 2p 20 ct that arrives at the FACP and land it in on main lugs of a say
that specs main wire range from
then send the original old1 and old 2 on their ways
and grab a new dedicated ct for facp?
The problem of course looks like I can't limit the open slot from being used :/
I could use it for another dedicated ct to run a service receptacle.
thanks!