Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
The answer in this electrical code calculations book has to be wrong
It ask what the minimum size NM cable to supply a 50 gallon storage type water heater. 240 volt single phase supply, non simultaneous upper and lower heating elements at 4500 watts. Second, it also ask what size 60/70 degree circuit breaker will be required
The book correctly calculated the NM branch circuit conductor at
4500 watt / 240 volt = 18.75 amperes
For continuous load 18.75 i x 1.25 = 23.44 i ampere conductor
Book correctly selects #10 AWG good for 30 amperes at 60 degrees
However, the continuous load is to be protected for 23.44 i amperes would equate to the next standard larger size OCPD (not over the ampacity of wire but over continuous load amperes) to be used at 25 ampere breaker but not a 30 ampere breaker selected by the book
In contradiction NEC does show a 10 AWG conductor being protected by a 30 ampere breaker for SMALL CONDUCTOR CODE, but should this mean that a larger ampacity conductor cannot be protected by a smaller OCPD breaker nor should a load be protected by an OCPD rated higher than the next higher standard size breaker
It ask what the minimum size NM cable to supply a 50 gallon storage type water heater. 240 volt single phase supply, non simultaneous upper and lower heating elements at 4500 watts. Second, it also ask what size 60/70 degree circuit breaker will be required
The book correctly calculated the NM branch circuit conductor at
4500 watt / 240 volt = 18.75 amperes
For continuous load 18.75 i x 1.25 = 23.44 i ampere conductor
Book correctly selects #10 AWG good for 30 amperes at 60 degrees
However, the continuous load is to be protected for 23.44 i amperes would equate to the next standard larger size OCPD (not over the ampacity of wire but over continuous load amperes) to be used at 25 ampere breaker but not a 30 ampere breaker selected by the book
In contradiction NEC does show a 10 AWG conductor being protected by a 30 ampere breaker for SMALL CONDUCTOR CODE, but should this mean that a larger ampacity conductor cannot be protected by a smaller OCPD breaker nor should a load be protected by an OCPD rated higher than the next higher standard size breaker