Minimum size of secondary conductor

Status
Not open for further replies.

KSue

Member
Location
Minnesota
Page 138- Understanding NEC V1

Question: What is the minimum size secondary conductor required for a 2-wire 480V to 120 transformer rated 1.5KV?

It gives the following answer:

Primary Current = 1500VA/480V= 3.13A
Primary Protection 3.13A x 1.67= 5.22A = 5A

The final answer comes to 12.5A secondary current, thus 14AWG, rated 20A at 60C.

Where did the 1.67 come from?
 

KSue

Member
Location
Minnesota
Thanx!!!

Thanx!!!

I knew one of guys knew... THANX!!! How about one more question..

Figure 240-19 defines feeder taps not over 10'

What does it mean "not less than 1/10th the ampacity of the device protecting it." :-?

Is it referring to the protection devices below the raceway, or the protection device of the feeder in the raceway? I don't know if you have online access to the picture itself, but maybe I said it clear enough here.. let me know.

Okay how about two quetions.

The 10' feeders are not < 1/10th the ampacity of the device protecting it.
The 25' feeders are not < 1/3rd the ampacity of the device protecting it.
The 100' feeders are not < 1/3rd the ampacity of the device protecting it.

What is the sigificance of these fractional values with respect to the circuit?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
A feeder can have a 10' tap which would require a tap conductor at least 1/10 of the ampacity of the feeder.

So a 200 amp feeder can be tapped up to 10' with a conductor that has an ampacity of at least 20 amps.

The 25' tap rule increases the tap conductors to 25' but now requires a minimum ampacity of the tap conductors to be 1/3 or greater than the ampacity of the feeder.

So a 300 amp feeder can be tapped up to 25' with a conductor that has an ampacity of at least 100 amps.


The 100' rule is for he special situation of high bay manufacturing buildings.
 