The only NEC reference I've found for "Conductor Bending Radius" is only for 1000V (600V in earlier versions) or greater. (Part II. Requirements for over 1000 Volts, Nominal - 300.34 -Conductor Bending Radius.) I found a THHN spec from the site listed below, but the spec for the Mfg. of wire they're using only states:
"3.1.4 Minimum Bend Radius: Bends in Type THHN shall be made so that the cable will not be damaged." - https://www.southwire.com/support/THHNGuideSpecifications.htm
I found another Mfg. that states:
"3.1.3 Minimum Bend Radius: The minimum bending radius of THHN when training into final position (with no tension on the cable) should be 4 times the cable diameter for 14 AWG - 500MCM and 5 times the cable diameter for 600–750 MCM. When pulling through conduit (under tension) the minimum bending radius should be increased to 8 times the cable diameter for 14 AWG – 500 MCM and 10 times the cable diameter for 600-750 MCM."
http://www.cerrowire.com/files/file/THHN Spec Sheet.pdf
Is there such a specification that is concrete such as a UL rating specification for THHN? I am going to reject this 480V-800A switchboard install because the minimum bending radius of most of these conductors is probably less that 2-3x Max the diameter of the conductor. I would just like a more solid reference to justify my rejection.
"3.1.4 Minimum Bend Radius: Bends in Type THHN shall be made so that the cable will not be damaged." - https://www.southwire.com/support/THHNGuideSpecifications.htm
I found another Mfg. that states:
"3.1.3 Minimum Bend Radius: The minimum bending radius of THHN when training into final position (with no tension on the cable) should be 4 times the cable diameter for 14 AWG - 500MCM and 5 times the cable diameter for 600–750 MCM. When pulling through conduit (under tension) the minimum bending radius should be increased to 8 times the cable diameter for 14 AWG – 500 MCM and 10 times the cable diameter for 600-750 MCM."
http://www.cerrowire.com/files/file/THHN Spec Sheet.pdf
Is there such a specification that is concrete such as a UL rating specification for THHN? I am going to reject this 480V-800A switchboard install because the minimum bending radius of most of these conductors is probably less that 2-3x Max the diameter of the conductor. I would just like a more solid reference to justify my rejection.