The pvc conduit with the communication cable (fiber or cat6) must be buried 18 inches as electrical ones?

Do I need a minimun separation between pvc electrical and pvc communication conduits?
 
Hi

The pvc conduit with the communication cable (fiber or cat6) must be buried 18 inches as electrical ones?

Do I need a minimun separation between pvc electrical and pvc communication conduits?
There is no minimum burial depth for communications. Strictly a design issue.

But there is a minimum required spacing between communications and power. Familiarize yourself with Article 800.
 