J jjavier Member Location Maine Apr 26, 2017 #1 Hi The pvc conduit with the communication cable (fiber or cat6) must be buried 18 inches as electrical ones? Do I need a minimun separation between pvc electrical and pvc communication conduits?
Hi The pvc conduit with the communication cable (fiber or cat6) must be buried 18 inches as electrical ones? Do I need a minimun separation between pvc electrical and pvc communication conduits?
Smart $ Esteemed Member Location Ohio Apr 26, 2017 #2 jjavier said: Hi The pvc conduit with the communication cable (fiber or cat6) must be buried 18 inches as electrical ones? Do I need a minimun separation between pvc electrical and pvc communication conduits? Click to expand... There is no minimum burial depth for communications. Strictly a design issue. But there is a minimum required spacing between communications and power. Familiarize yourself with Article 800.
jjavier said: Hi The pvc conduit with the communication cable (fiber or cat6) must be buried 18 inches as electrical ones? Do I need a minimun separation between pvc electrical and pvc communication conduits? Click to expand... There is no minimum burial depth for communications. Strictly a design issue. But there is a minimum required spacing between communications and power. Familiarize yourself with Article 800.