OK a ETL listed 1.5T minisplit nameplate says use 20a breaker, double pole 240V. That's as we know #12. But the install manual claims #14/3 to the indoor unit. Now we know the indoor unit only takes a few amps at most and there's no other loads so #14 is fine for that application. But all there is on the condenser is a relay connected across the incoming line to control the fan and electronics. No internal fuse.
So by strict letter of the code, shouldn't that run from the condenser to the indoor unit need to be #12/3? This is no different than using #14 for switch legs on a 20a circuit - which is illegal?
How can this be listed that way. I think the manual is a mistake and the listing just overlooked that.
The NEC need to look at these minisplits in more details fro the next code cycle. Also the use of 14/4 SO should be banned as well unless the wire is specifically listed for in-wall use?
So by strict letter of the code, shouldn't that run from the condenser to the indoor unit need to be #12/3? This is no different than using #14 for switch legs on a 20a circuit - which is illegal?
How can this be listed that way. I think the manual is a mistake and the listing just overlooked that.
The NEC need to look at these minisplits in more details fro the next code cycle. Also the use of 14/4 SO should be banned as well unless the wire is specifically listed for in-wall use?