T tracker1474 New User Location Washington Occupation Electrician Nov 28, 2023 #1 How do you calculate the amps for 5 equal secondary tie ins to a 1,500 amp transformer? With code reference please
How do you calculate the amps for 5 equal secondary tie ins to a 1,500 amp transformer? With code reference please
petersonra Senior Member Location Northern illinois Occupation engineer Nov 28, 2023 #2 1500/5? Does not seem like a code issue as such. Perhaps information would help us understand what you are actually wanting to know.
1500/5? Does not seem like a code issue as such. Perhaps information would help us understand what you are actually wanting to know.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Nov 28, 2023 #3 Not enough information.
roger Moderator Staff member Location Fl Occupation Retired Electrician Nov 28, 2023 #4 I agree that it seems like missing info but I wonder if it boils down to 450.6(A)(1)
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 28, 2023 #5 Are you asking about 5 sets of parallel conductors for a 1500 amp circuit? If so you would need 5 sets of 300 amp conductors.
Are you asking about 5 sets of parallel conductors for a 1500 amp circuit? If so you would need 5 sets of 300 amp conductors.