I live in rural MO and I CONSTANTLY see the service wires ran to a disconnect under or adjacent to the meter
wires are then ran from the load side of that first disconnect to the house with NO EGC
then inside the house a #6 AWG bare copper is ran from a ground rod to the neutral bar or a bar bonded to the neutral bar (if you’re lucky to find one like this)
Then ALL the neutral conductor’s are landed on the neutral bar with ALL the EGC’s of the branch circuits ran in the home.
It really bothers me that there is no EGC from the first disconnect to the house and landed on a SEPARATE bar and then connect a GEC from the ground rod to the isolated ground bar and land all the EGC’s to this bar (Please let me know if I can describe the set up more clearly if I have not explained it correctly)
For the life of me I cannot describe the consequence of this to the people doing it, that should mean the system won’t clear a fault, is that correct?
I have yet to test it out, but I have seen breakers tripping in homes with this setup.
What am I missing here?
How can I be clear about the negative effect of running a service to a home without an EGC from the source?
wires are then ran from the load side of that first disconnect to the house with NO EGC
then inside the house a #6 AWG bare copper is ran from a ground rod to the neutral bar or a bar bonded to the neutral bar (if you’re lucky to find one like this)
Then ALL the neutral conductor’s are landed on the neutral bar with ALL the EGC’s of the branch circuits ran in the home.
It really bothers me that there is no EGC from the first disconnect to the house and landed on a SEPARATE bar and then connect a GEC from the ground rod to the isolated ground bar and land all the EGC’s to this bar (Please let me know if I can describe the set up more clearly if I have not explained it correctly)
For the life of me I cannot describe the consequence of this to the people doing it, that should mean the system won’t clear a fault, is that correct?
I have yet to test it out, but I have seen breakers tripping in homes with this setup.
What am I missing here?
How can I be clear about the negative effect of running a service to a home without an EGC from the source?