Minuteman
Senior Member
- Location
- The Sooner Nation
Doing a large add on to a house. The service is being upgraded and relocated. A disconnect was added next to the new mater base and new conductors ran to the old main panel (now a sub panel).
My question arises from the neutral and ground bars in the panel. About half the neutrals and half the grounds were on landed on the two bars. The bar on the left had the neutral feed, the bar on the right had only the bond wire or the copper water line. There was no jumper between the two bars and neither side had a bond jumper or screw to bond the panel.
So, am I to assume that the only neutral path that the neutrals on the right had was through the water pipe and/or the nipple between the panel and the old meter base? I would guess that there would have been voltage problems if several of the right side neutrals where under load at the same time.
My question arises from the neutral and ground bars in the panel. About half the neutrals and half the grounds were on landed on the two bars. The bar on the left had the neutral feed, the bar on the right had only the bond wire or the copper water line. There was no jumper between the two bars and neither side had a bond jumper or screw to bond the panel.
So, am I to assume that the only neutral path that the neutrals on the right had was through the water pipe and/or the nipple between the panel and the old meter base? I would guess that there would have been voltage problems if several of the right side neutrals where under load at the same time.