jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
So I'm involved in sizing a battery backup system where the customer wants to run the air-conditioner on the backup. (Don't criticize please.
)
Attached is the label for the compressor unit. The LRA is missing, and I want to check my sanity that the proposed battery system can deal with the inrush current of this unit. The battery system has a peak power (surge) rating of 11.4kVA for 10 seconds. I think this is sufficient? We could propose higher if needed.
My understanding is that the LRA is locked rotor amps, and that this is for practical purposes equivalent to motor-starting current for a fraction of a second. Correct? Also is the LRA listed on the unit because it's (apparently) a DC motor ?
My understanding is also that the motor-starting current is always higher than the FLA.
Is there any kind of rule of thumb on ratio of LRA to FLA such that I can make a conservative guess on the requirement here? Alternatively, if I use the max OCPD rating is that not conservative enough?
Finally, if this compressor handles linesets for multiple airhandlers (zones) in the house, how do you think the compressor amps would vary if only a portion of them are turned on?
Your thoughts appreciated.
Attached is the label for the compressor unit. The LRA is missing, and I want to check my sanity that the proposed battery system can deal with the inrush current of this unit. The battery system has a peak power (surge) rating of 11.4kVA for 10 seconds. I think this is sufficient? We could propose higher if needed.
My understanding is that the LRA is locked rotor amps, and that this is for practical purposes equivalent to motor-starting current for a fraction of a second. Correct? Also is the LRA listed on the unit because it's (apparently) a DC motor ?
My understanding is also that the motor-starting current is always higher than the FLA.
Is there any kind of rule of thumb on ratio of LRA to FLA such that I can make a conservative guess on the requirement here? Alternatively, if I use the max OCPD rating is that not conservative enough?
Finally, if this compressor handles linesets for multiple airhandlers (zones) in the house, how do you think the compressor amps would vary if only a portion of them are turned on?
Your thoughts appreciated.