Missing neutral

Status
Not open for further replies.

High Peak

Member
On a multi-tap 175W high pressure sodium wallpack wired for 120V, if there are six fixtures on one circuit with the neutral unattached, would the lights, ballasts and lamps burn out or would the lights just not work? When re-attached, would the fixtures work and, if so, would there be any damage?
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
On a multi-tap 175W high pressure sodium wallpack wired for 120V, if there are six fixtures on one circuit with the neutral unattached, would the lights, ballasts and lamps burn out or would the lights just not work? When re-attached, would the fixtures work and, if so, would there be any damage?

If they are not connected to a MWBC, sure, hook the neutral up and no problems. If it is a MWBC, I would bet they would come back to life. Those transformers tend to be forgiving.
 

vinster888

Senior Member
i would think the fixtures should be fine they just wouldnt light. attach neutral and you should be good. unless you had a hot phase come in contact with the fixture end of said broken neutral. then you most likely will have an issue.
 

High Peak

Member
missing neutral

missing neutral

We were told that the lamps would burn out and the ballasts would be severely burnt and damaged.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So you have 120 volts feeding six fixtures and you lose the neutral. The lights would just go out since you wouldn't have a complete circuit.
 