We are installing 6 Mitsubishi split a/c units. 6 outdoor units, with 6 corresponding indoor units to cool electric rooms and i.t rooms. The outdoor units are 208 volt single phase fed from 20 or 30 amp breakers, depending on size of unit, as per manufacturer. The branch circuits land on L1 and L2 in the outdoor unit. According to the installation manual and the HVAC tech onsite, the outdoor unit wiring going to the indoor unit needs to have 3 conductors 16 AWG. These terminals are labeled S1, S2, S3 at both indoor and outdoor units. The "Field electrical wiring" chart in manual shows 208V between S1-S2, and 24VDC between S2-S3. No idea how this is accomplished or what S1-S3 might read. The problem is, there is no protection in the outdoor unit for the 16 AWG conductors to go to the indoor unit. They are protected only by our breakers ahead of the outdoor unit. The HVAC tech insists they have to be wired this way for the 24VDC communication to work, and they've had problems with the indoor units not running correctly when wired with 12 or 10 AWG wiring. I say, I can't run 16 AWG protected by a 30 amp breaker. The wiring has been done already, to code (12 & 10 AWG). Now the HVAC tech says he can't do start up on the units because we haven't wired them per manufacturers instructions (16 AWG to indoor units). We're at a bit of a stalemate now. Has anybody run into this, or dealt with these units much? We've installed them previously, and never had a problem that we know of.