I have a commercial customer with CH 200Amp 65K AIC rated main breaker. We need to add another sub next to it for more breaker space. I am wondering if I can do SQUARE-D with 22K AIC rated panel.
Also, any code issue that you see with this install? I could not find any code sections that I am violating, but I am still searching.
- Does the 2nd panel have to be CH with 65K AIC rating?
- SQUARE-D is OK but has to be 65K AIC rating
- SQUARE-D is fine and can be 22K AIC rated, because it will be in series with the main CH breaker that is rated at 65K AIC.
Also, any code issue that you see with this install? I could not find any code sections that I am violating, but I am still searching.