Yes as long as the available fault current is less than the lowest rated breaker. The 10K rated breaker would lead one to believe that there is less than 10K available. But then why have far more costly higher rated breakers in the same panel? Makes no sense to me.
No.That makes two of us
Question, is a series combination is used, the main OCPD must be in the panel, correct?
Yeah you won't find a series rating that will go from a 1600 frame device all the way down to 10 k. Typically only 250 amp frame or less will have ratings down to 10K.Even better
Still have to run a fault calc though, 1600 amps main... 10kaic seems to be pushing it.
Many designers have default AIC ratings which they use in their specs, like 65kAIC at 480V, as the available fault is often not known until the POCO delivers a transformer. Once the contractor knows that the spec'd and approved equipment is okay they rarely ask for a change order to supply lower rated devices.Yes as long as the available fault current is less than the lowest rated breaker. The 10K rated breaker would lead one to believe that there is less than 10K available. But then why have far more costly higher rated breakers in the same panel? Makes no sense to me.
I understand that. But why have mixed values in the same panel?Many designers have default AIC ratings which they use in their specs, like 65kAIC at 480V, as the available fault is often not known until the POCO delivers a transformer. Once the contractor knows that the spec'd and approved equipment is okay they rarely ask for a change order to supply lower rated devices.
Yeah you won't find a series rating that will go from a 1600 frame device all the way down to 10 k. Typically only 250 amp frame or less will have ratings down to 10K.
Original project supplied with 65k breakers per boilerplate specs. NEC required label showing available fault current of 9kA. During an expansion the new contractor adds circuits with breakers with standard AIC ratings of 10k and 22k.
Yeah it almost looks like they ran their calcs and are showing values for downstream devices within MDP. On another note, are the 60A's fed from a 2000A possible? Without larger amp electronic trip unit turned down to 60A that is.Another possibility is that a junior engineer thought you selected interrupting capacity based on downstream requirements rather than source.