Does this comply with the NEC? I don't believe so, but I can't find a reference to this kind of arrangement. This is from a new 4oo amp, 480 volt, 4 wire service supplying high school football field lighting. My question concerns a branch circuit supplying security lights behind the bleachers on opposite sides of the field. A 15 amp, 2 pole breaker in the 4oo amp panel passes through a contact of a lighting contactor then to terminal blocks where it is split. One pair of 480 volt single phase conductors leaves the terminal blocks and supplies 4 400w luminaires behind the West bleachers. Another pair of conductors leave the same terminal blocks along with a neutral conductor from the same panel board, and supply 2 277 volt circuits to 12 70w luminaires behind the East bleachers.