Ok,
You have conduit run with 6 conductors (THHN stranded 600 V wire). The client wants to use 4 conductors for 120 volt circuit and 2 conductors for 24 Volt AC control wire (let?s say to energize a 24 volt holding coil on a contactor)
Guy #1 says ?you can?t run low voltage and 120 volts in the same pipe. 24 volts is a class 2 circuit and can?t be run with a class 1 circuit?
Guy # 2 says ?the wire is rated for a class 1 circuit and the conductors are pulled, we don?t have a problem. Wire it up and its fine.? He does agree if it was a class 2 wire such as thermostat wire it would be unacceptable but it clearly is not, so you are fine.
Guy #1 state the 24 volt control transformer is a Class 2 transformer so it is a class 2 circuit, regardless of wire type and rating and can?t be mixed with class 1.
Who is correct?
Expanding this.
The customer wants to pull a Belden Shielded cable (9418) http://www.belden.com/techdatas/metric/9418.pdf cable in the same conduit. It is intended to be used for a 4-20 mA signal intended modulate a VFD.
Is it allowed in the same conduit?
You have conduit run with 6 conductors (THHN stranded 600 V wire). The client wants to use 4 conductors for 120 volt circuit and 2 conductors for 24 Volt AC control wire (let?s say to energize a 24 volt holding coil on a contactor)
Guy #1 says ?you can?t run low voltage and 120 volts in the same pipe. 24 volts is a class 2 circuit and can?t be run with a class 1 circuit?
Guy # 2 says ?the wire is rated for a class 1 circuit and the conductors are pulled, we don?t have a problem. Wire it up and its fine.? He does agree if it was a class 2 wire such as thermostat wire it would be unacceptable but it clearly is not, so you are fine.
Guy #1 state the 24 volt control transformer is a Class 2 transformer so it is a class 2 circuit, regardless of wire type and rating and can?t be mixed with class 1.
Who is correct?
Expanding this.
The customer wants to pull a Belden Shielded cable (9418) http://www.belden.com/techdatas/metric/9418.pdf cable in the same conduit. It is intended to be used for a 4-20 mA signal intended modulate a VFD.
Is it allowed in the same conduit?