Mixed Voltages
I am clueless on MV installs but there is this:
300.3(C)
(2) Over 1000 Volts, Nominal. Conductors of circuits
rated over 1000 volts, nominal, shall not occupy the same
equipment wiring enclosure, cable, or raceway with conductors
of circuits rated 1000 volts, nominal, or less unless
otherwise permitted in 300.3(C)(2)(a) through (C)(2)(d).
(a) Primary leads of electric-discharge lamp ballasts insulated
for the primary voltage of the ballast, where contained
within the individual wiring enclosure, shall be permitted
to occupy the same luminaire, sign, or outline
lighting enclosure as the branch-circuit conductors.
(b) Excitation, control, relay, and ammeter conductors
used in connection with any individual motor or starter
shall be permitted to occupy the same enclosure as the
motor-circuit conductors.
(c) In motors, transformers, switchgear, switchboards,
control assemblies, and similar equipment, conductors of
different voltage ratings shall be permitted.
(d) In manholes, if the conductors of each system are
permanently and effectively separated from the conductors
of the other systems and securely fastened to racks, insulators,
or other approved supports, conductors of different
Conductors having nonshielded insulation and operating
at different voltage levels shall not occupy the same
enclosure, cable, or raceway.
I think the original post had a typo. I think the two voltages are 480V and 13.8KV. If that is the case, then I doubt you will find a cable intended for use in a 480V system that has a voltage rating of 15kV. So no, you can't do it.