Mixing 480 volt and 120 volt.

Status
Not open for further replies.

jeff1166

Member
Where in the code book can I find mixing voltages in a gutter. I want to know if is legal to install 480-volt circuits and 120-volt circuits in the same gutter. The gutter is mounted above the two different panels. I want to use one long gutter for both panels.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Mixing 480 volt and 120 volt.

Its done all the time. But take a look at Art 200 on identification of grounded conductors for more than one system, it may be 200.5...one neutral is white the other has a stripe.
 

jeff1166

Member
Re: Mixing 480 volt and 120 volt.

Iwire and Tom, Thanks alot for your help. I am a new member and appreciate the service you guys are providing.
 

steve65

Member
Re: Mixing 480 volt and 120 volt.

as long as both panels are from the same service there is nothing wrong with it
 

steve65

Member
Re: Mixing 480 volt and 120 volt.

dont have code book with me left at job site will bring it home tomorrow and tell you code article have many people say you cant run 120 and 480 in same pipe code book does say that as long as they are from the same service it can be done.
 