So when does secondary transformer protection occur with a downstream panelboard Main Breaker? ???????????????????
This is secondary conductor protection.When it's location and size comply with 240.21.
That's the subject and what I'm trying to check. Is there a Code section that confirms this understanding?AFAIK a downstream breaker will always be considered to protect the transformer secondary (presuming suitable primary protection as well).
When the Main Breaker is sized per the "Secondary Protection" column of Table 450.3(B).So when does secondary transformer protection occur with a downstream panelboard Main Breaker? ???????????????????
What are you asking then? The only other component on the secondary side is the windings and they don't get overcurrent protection. The only other required protection is primary protection.This is secondary conductor protection.
Can you post those? some of us don't have that handbook.What has had me befuddeled is the Exhibits 450.4 and Exhibits 450.5 in the NECHB (2014). Especially 450.5 where is shows an OCP fuse outside the panelboard.....
Thank you for all your responses!!!
Keep in mind per NEC terminology the "panelboard" is the assembly of bus bars and overcurrent devices, the enclosure it is all installed inside of is a "cabinet". That there is just a one line diagram showing the order of items with little other details. Might have been better had the author drawn bus bar and ocpd's instead of a cabinet though. But also keep in mind the handbook is not an official NFPA interpretation of the NEC content just that of those that authored it - says this somewhere right in the front matter of the book as well.