Does anyone typically come across 480V LV switchgear that is MLO without a main breaker. I recently did a project where the main breaker was omitted due to space limitations on a unit substation and in its place were CT's and an overcurrent relay which transfer tripped the upstream MV feeder breaker.
I'm assuming that the secondary CT's and relay provide the required secondary transformer and cable protection as required per the NEC. (I don't know if secondary transformer protection is even required due to this being in a supervised location).
The part that is unclear to me is the requirement in 225.31 and 225.32 that require a building to have a disconnecting means if this MLO switchgear is located in a separate building. 225.32 exception 1 states that if the facility has qualified personell then the disconnecting means can be located elsewhere and is not necessarily required to be located at the Switcghear in the building. Does this mean that this MLO switchgear is ok in a separate building in a supervised facility.
Also in terms of Arc Flash protection I believe that transfer tripping to upstream breaker will provide the same level of AF protection as would a LV main breaker.
Would the secondary CT's and relay also meet the requirement for ground fault protection in 230.95?
I'm assuming that the secondary CT's and relay provide the required secondary transformer and cable protection as required per the NEC. (I don't know if secondary transformer protection is even required due to this being in a supervised location).
The part that is unclear to me is the requirement in 225.31 and 225.32 that require a building to have a disconnecting means if this MLO switchgear is located in a separate building. 225.32 exception 1 states that if the facility has qualified personell then the disconnecting means can be located elsewhere and is not necessarily required to be located at the Switcghear in the building. Does this mean that this MLO switchgear is ok in a separate building in a supervised facility.
Also in terms of Arc Flash protection I believe that transfer tripping to upstream breaker will provide the same level of AF protection as would a LV main breaker.
Would the secondary CT's and relay also meet the requirement for ground fault protection in 230.95?