A new member has a few questions regarding an old post. I created this thread for him.
Regarding this thread:
http://forums.mikeholt.com/showthread.php?t=150617&p=1457020#post1457020
He asks the following:
I have a few questions about this thread:
1. Isn't the sub panel ALREADY protected to 80A by the 80 breaker in the main panel?
2. Is the logic of installing a 80A Main breaker in the 125a sub panel that it is permanent and cannot be as easily removed for a larger breaker as the 80a breaker in the main?
3. In the event there are no loads on the sub, and the PV is fully cranking close to 60A, does that not mean that the 60a will be backfed through the 80a in the main 200a panel which, in and of itself, would have a backfeed limit of 40a according to the 120% rule?
Any light on this would be most helpful. thx
Regarding this thread:
http://forums.mikeholt.com/showthread.php?t=150617&p=1457020#post1457020
He asks the following:
I have a few questions about this thread:
1. Isn't the sub panel ALREADY protected to 80A by the 80 breaker in the main panel?
2. Is the logic of installing a 80A Main breaker in the 125a sub panel that it is permanent and cannot be as easily removed for a larger breaker as the 80a breaker in the main?
3. In the event there are no loads on the sub, and the PV is fully cranking close to 60A, does that not mean that the 60a will be backfed through the 80a in the main 200a panel which, in and of itself, would have a backfeed limit of 40a according to the 120% rule?
Any light on this would be most helpful. thx