Yes. The Emergency Disconnect Circuit Breaker at the Utility MeterDepends. Is there is an OCPD ahead of the panel? If so there is no limit as to the length.
Then the conductors going to the panel are feeder conductors so there is no length or nearest the point of entry restrictions.Yes. The Emergency Disconnect Circuit Breaker at the Utility Meter
What difference does it make how/whether it is marked? If there is OCPD, the conductors are a feeder.As long as it is marked "EMERGENCY DISCONNECT, SERVICE DISCONNECT" there is no distance as the load side conductors are feeder conductors and not service conductors.
It was a fiat by the CMP in charge of Article 230 for the 2020 and 2023 NEC. The label can make the "emergency disconnect" be considered "not service equipment", which means that you don't need a separate EGC run downstream of the emergency disconnect. This was to facilitate retrofitting an exterior emergency disconnect for existing installs with an interior service disconnect. And this is all going away in the 2026 NEC, it will simply require the service disconnect to be exterior on one and two family dwellings.What difference does it make how/whether it is marked? If there is OCPD, the conductors are a feeder.
If it is marked "EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT" the conductors on the load side are still service conductors even if there is an OCPD. This marking is used when you don't want to relocate the grounding and bonding connections from the inside panel to the outside panel.What difference does it make how/whether it is marked? If there is OCPD, the conductors are a feeder.
which makes this thread even more confusingIf it is marked "EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT" the conductors on the load side are still service conductors even if there is an OCPD. This marking is used when you don't want to relocate the grounding and bonding connections from the inside panel to the outside panel.
I have seen new installs where the Contractor has ran just 3 wires from the Emergency Disconnect to the panel inside. They were approved. The GEC in these for instances originated from the panel inside the house.If it is marked "EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT" the conductors on the load side are still service conductors even if there is an OCPD. This marking is used when you don't want to relocate the grounding and bonding connections from the inside panel to the outside panel.
Yes...just put the correct marking on the EM disconnect. This was such a screwed up rule, 230.85 goes away in the 2026 and it will simply require the service disconnect for one- and two-family dwellings to be outside, either mounted to the dwelling or within sight.I have seen new installs where the Contractor has ran just 3 wires from the Emergency Disconnect to the panel inside. They were approved. The GEC in these for instances originated from the panel inside the house.
I’ve been installing with a 4 wire feeder to the panel with GEC from the outside disconnect and bonding screw/ strap attached at that point.
Are both ways code compliant?