MLO panel vs Main Breaker

nizak

Senior Member
Is there a distance requirement as to how far away the Emergency Disconnect can be located on a residence in relation to a 40 space MLO panel without a main breaker installed in the basement?

Thank you.
 
As long as it is marked "EMERGENCY DISCONNECT, SERVICE DISCONNECT" there is no distance as the load side conductors are feeder conductors and not service conductors.
 
As long as it is marked "EMERGENCY DISCONNECT, SERVICE DISCONNECT" there is no distance as the load side conductors are feeder conductors and not service conductors.
What difference does it make how/whether it is marked? If there is OCPD, the conductors are a feeder.
 
What difference does it make how/whether it is marked? If there is OCPD, the conductors are a feeder.
It was a fiat by the CMP in charge of Article 230 for the 2020 and 2023 NEC. The label can make the "emergency disconnect" be considered "not service equipment", which means that you don't need a separate EGC run downstream of the emergency disconnect. This was to facilitate retrofitting an exterior emergency disconnect for existing installs with an interior service disconnect. And this is all going away in the 2026 NEC, it will simply require the service disconnect to be exterior on one and two family dwellings.

I guess a more generous way to put the rules in the 2020 and 2023 NEC is flexibility on the location of the MBJ. If there is an exterior emergency disconnect, you are still allowed to install the MBJ on a downstream panel that meets the location requirements for a service disconnect.

Cheers, Wayne
 
What difference does it make how/whether it is marked? If there is OCPD, the conductors are a feeder.
If it is marked "EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT" the conductors on the load side are still service conductors even if there is an OCPD. This marking is used when you don't want to relocate the grounding and bonding connections from the inside panel to the outside panel.
 
If it is marked "EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT" the conductors on the load side are still service conductors even if there is an OCPD. This marking is used when you don't want to relocate the grounding and bonding connections from the inside panel to the outside panel.
which makes this thread even more confusing :)
 
If it is marked "EMERGENCY DISCONNECT, NOT SERVICE EQUIPMENT" the conductors on the load side are still service conductors even if there is an OCPD. This marking is used when you don't want to relocate the grounding and bonding connections from the inside panel to the outside panel.
I have seen new installs where the Contractor has ran just 3 wires from the Emergency Disconnect to the panel inside. They were approved. The GEC in these for instances originated from the panel inside the house.

I’ve been installing with a 4 wire feeder to the panel with GEC from the outside disconnect and bonding screw/ strap attached at that point.

Are both ways code compliant?
 
I have seen new installs where the Contractor has ran just 3 wires from the Emergency Disconnect to the panel inside. They were approved. The GEC in these for instances originated from the panel inside the house.

I’ve been installing with a 4 wire feeder to the panel with GEC from the outside disconnect and bonding screw/ strap attached at that point.

Are both ways code compliant?
Yes...just put the correct marking on the EM disconnect. This was such a screwed up rule, 230.85 goes away in the 2026 and it will simply require the service disconnect for one- and two-family dwellings to be outside, either mounted to the dwelling or within sight.
 