G Gategator37 Senior Member Oct 5, 2010 #1 Does a MLO branch circuit panel have to be within sight of its disconnect or can the MDP be in a separate area than the MLO branch circuit panel? Thanks
Does a MLO branch circuit panel have to be within sight of its disconnect or can the MDP be in a separate area than the MLO branch circuit panel? Thanks
iwire Moderator Staff member Location Massachusetts Oct 5, 2010 #2 Gategator37 said: Does a MLO branch circuit panel have to be within sight of its disconnect Click to expand... Nope or can the MDP be in a separate area than the MLO branch circuit panel? Click to expand... Yes, as long as it is in the same building or structure.
Gategator37 said: Does a MLO branch circuit panel have to be within sight of its disconnect Click to expand... Nope or can the MDP be in a separate area than the MLO branch circuit panel? Click to expand... Yes, as long as it is in the same building or structure.