Re: MLO panels
cartman
In general, you could use main lug panels in each of the 6 stores. You would need mains, service disconnects, grouped together at the meter stack. Look for MCB's where you need overcurrent protection or where you need a disconnect.
Hurk27 is correct, if the construction is such that the walls dividing each store are firewalls with certain specific ratings, each store could be a separate building or structure. Individual stores will almost always be separated by a firewall of some rating, but where I work, in a commercial building the firewall has to be a 3hr or 4hr wall before it is considered a separate building or structure and therefor would require a main breaker. Otherwise it is an area separation wall and does not create a separate building. This is up to the AHJ though.
Jim T