This is a follow up to the 15 page thread from about a month ago. . My last post on that thread was:
This update has been awhile in coming. . The UL Engineer in charge of the Panelboard Marking Guide and also on Code Making Panel #9, Robert Osborne, referred me to his AHJ Regulatory Services staff member, Tom Lichtenstein, to call and work thru this issue.
At the beginning of our conversation, when he found out we were going to be discussing a single panel installation, he said we needed to go to 408 before we go to 230. . Basically there are 3 different main OCD requirements. . To make it easier to refer to each type, I?m going to designate them as AAA, BBB, & CCC.
AAA: Lighting and Appliance Branch-Circuit Panelboard
408.34(A), ?Lighting and Appliance Branch-Circuit Panelboard. . A lighting and appliance branch-circuit panelboard is one having more than 10 percent of its overcurrent devices protecting lighting and appliance branch circuits.?
408.34 second sentence, ?A lighting and appliance branch circuit is a branch circuit that has a connection to the neutral of the panelboard and that has overcurrent protection of 30 amperes or less in one or more conductors.?
In short
Lighting and Appliance Branch-Circuit Panelboard
more than 10 percent are
. . 1) circuit that has a connection to the neutral
. . 2) overcurrent protection of 30 amperes or less
BBB: Power Panelboard
408.34(B), ?A power panelboard is one having 10 percent or fewer of its overcurrent devices protecting lighting and appliance branch circuits.?
In short
Power Panelboard
10 percent or fewer are
. . 1) circuit that has a connection to the neutral
. . 2) overcurrent protection of 30 amperes or less
CCC: Power Panelboard
408.36(B), ?Power Panelboard Protection. ?.. A power panelboard with supply conductors that include a neutral, and having more than 10 percent of its overcurrent devices protecting branch circuits rated 30 amperes or less?.
In short
Power Panelboard
panel supply conductors that include a neutral
more than 10 percent are
overcurrent protection of 30 amperes or less
but among all of the OCDs of 30a or less, those circuits that use a neutral do not total more than 10% of the total OCDs or else the panel would be classified as a lighting and appliance branch circuit panel.
So first it needs to be determined how the panel is being used in the specific installation in question. . It?s the usage that determines the panel classification not something particular to the panel itself. . For a Service Main MLO:
If the panel usage is AAA, then it?s required to be limited to 2 main OCDs, 408.36(A)
If the panel usage is BBB, then you move on to 230.71
If the panel usage is CCC, it would first appear to be limited to one main OCD, 408.36(B), but because of 408.36(B)x, you move on to 230.71
The one thing that didn?t come out in the last thread about this subject was how the 10% figure is determined. . Mike the pitbull touched on it here
http://www.mikeholt.com/code_forum/showthread.php?p=605731#post605731
That post #122 in part said
He corrected himself later to specify that he was talking about the 10% figure from 408.34(A). . The 10% only looks at the 30a or less and the panel in question was a MLO with the following size breakers: 200a, 200a, 100a, 60a, 40a, & 30a. . Boa constrictor Mike was looking at the 30a breaker which was 1/6 or 16% of the breakers in the panel. . If the circuit on the 30a did use a neutral, it would be a lighting and appliance panel and restricted by 408.36(A) to 2 mains. . If the circuit on the 30a didn?t use a neutral, it would apparently be a power panel and not restricted to 2 mains.
Tom Lichtenstein added to the discussion that the 5 other breakers would also have to be taken into consideration. . I believe the 60a & the 40a were meant to feed AC units [without neutrals] but both 200a and possibly also the 100a were feeding subpanels. . Those panels by usage were lighting and appliance panels so the 200a breakers in the MLO main were protecting lighting and appliance branch circuits.
In the final analyses, his point was that a Service main panel with more than 2 mains could never be used in a residence because the loads are always over 10% lighting and appliance branch circuits.
David
dnem said:I approached the code making panel members at the Akron IAEI meeting last night, Oran Post panel#6, Tom Moore panel #11, and Tim McClintock newly appointed to panel #12. Tom got sidetracked before he could answer and I never caught up with him again. Tim wasn't sure and deferred to Oran. Oran was sure that the max 6 limit applied to capability, not just presently installed, but he wasn't familiar with the panelboard marking guide. Both Tim and Oran urged me to contact Robert Osborne who wrote the guide. So that's what I'm going to do.
This update has been awhile in coming. . The UL Engineer in charge of the Panelboard Marking Guide and also on Code Making Panel #9, Robert Osborne, referred me to his AHJ Regulatory Services staff member, Tom Lichtenstein, to call and work thru this issue.
At the beginning of our conversation, when he found out we were going to be discussing a single panel installation, he said we needed to go to 408 before we go to 230. . Basically there are 3 different main OCD requirements. . To make it easier to refer to each type, I?m going to designate them as AAA, BBB, & CCC.
AAA: Lighting and Appliance Branch-Circuit Panelboard
408.34(A), ?Lighting and Appliance Branch-Circuit Panelboard. . A lighting and appliance branch-circuit panelboard is one having more than 10 percent of its overcurrent devices protecting lighting and appliance branch circuits.?
408.34 second sentence, ?A lighting and appliance branch circuit is a branch circuit that has a connection to the neutral of the panelboard and that has overcurrent protection of 30 amperes or less in one or more conductors.?
In short
Lighting and Appliance Branch-Circuit Panelboard
more than 10 percent are
. . 1) circuit that has a connection to the neutral
. . 2) overcurrent protection of 30 amperes or less
BBB: Power Panelboard
408.34(B), ?A power panelboard is one having 10 percent or fewer of its overcurrent devices protecting lighting and appliance branch circuits.?
In short
Power Panelboard
10 percent or fewer are
. . 1) circuit that has a connection to the neutral
. . 2) overcurrent protection of 30 amperes or less
CCC: Power Panelboard
408.36(B), ?Power Panelboard Protection. ?.. A power panelboard with supply conductors that include a neutral, and having more than 10 percent of its overcurrent devices protecting branch circuits rated 30 amperes or less?.
In short
Power Panelboard
panel supply conductors that include a neutral
more than 10 percent are
overcurrent protection of 30 amperes or less
but among all of the OCDs of 30a or less, those circuits that use a neutral do not total more than 10% of the total OCDs or else the panel would be classified as a lighting and appliance branch circuit panel.
So first it needs to be determined how the panel is being used in the specific installation in question. . It?s the usage that determines the panel classification not something particular to the panel itself. . For a Service Main MLO:
If the panel usage is AAA, then it?s required to be limited to 2 main OCDs, 408.36(A)
If the panel usage is BBB, then you move on to 230.71
If the panel usage is CCC, it would first appear to be limited to one main OCD, 408.36(B), but because of 408.36(B)x, you move on to 230.71
The one thing that didn?t come out in the last thread about this subject was how the 10% figure is determined. . Mike the pitbull touched on it here
http://www.mikeholt.com/code_forum/showthread.php?p=605731#post605731
That post #122 in part said
jwelectric said:408.36(A) states that a lighting and appliance panelboard must be protected by not more than two mains.
In your panel as outlined above you have one thirty amp breaker which would constitute 1.2% of the Overcurrent devices in that panel.
If this 30 amp breaker supplies a circuit that also utilizes the neutral then this is a lighting and appliance panel and would require a main.
If this 30 amp breaker supplies a circuit that does not utilize the neutral then it is a power panelboard and does not require a main.
He corrected himself later to specify that he was talking about the 10% figure from 408.34(A). . The 10% only looks at the 30a or less and the panel in question was a MLO with the following size breakers: 200a, 200a, 100a, 60a, 40a, & 30a. . Boa constrictor Mike was looking at the 30a breaker which was 1/6 or 16% of the breakers in the panel. . If the circuit on the 30a did use a neutral, it would be a lighting and appliance panel and restricted by 408.36(A) to 2 mains. . If the circuit on the 30a didn?t use a neutral, it would apparently be a power panel and not restricted to 2 mains.
Tom Lichtenstein added to the discussion that the 5 other breakers would also have to be taken into consideration. . I believe the 60a & the 40a were meant to feed AC units [without neutrals] but both 200a and possibly also the 100a were feeding subpanels. . Those panels by usage were lighting and appliance panels so the 200a breakers in the MLO main were protecting lighting and appliance branch circuits.
In the final analyses, his point was that a Service main panel with more than 2 mains could never be used in a residence because the loads are always over 10% lighting and appliance branch circuits.
David