J Allan
- McHenry, Md
Per 550.33 (A) (1) Why are Feeder Grounding Conductor (EGC) for Mobil Homes required to be insulated.
Some jobs the Contractor or Homeowners install SER cable, after awhile you see a little bit of everything, especially with Homeowners. The one the other day the Pedestal for the Meter and disconnect was only 12" from the Mobil Home, and the Contractor installed SER Cable in a 3" Conduit above grade to the inside Panel, so would that be allowed, as the ground is not insulated, but it goes to a Mobil Home. What are your thoughts ? Also as I mentioned previously, when a Mobil Home is on a foundation and SER Cable is used to the Panel is that allowed. As I do not know why a insulated ground is required, I am not making an educated decision. I understand why an insulated ground is required for a Feeder for a Pool House, but not a Mobil Home. I agree with Fred B I would probably have to go to the original Code Committee hearing notes.
No ser whether installed in a conduit or not does not have an insulated equipment grounding conductor. There is a difference between covered and insulated. Ser has a covered ground but not an insulated ground.
To be fair, you did ask about SER!I know that, we are getting off base. I feel like I am on a job site. My question is the first Post.
Wow, you asked question about SER- which is, as you say, off topic, you get a response and then you get upset. Remember many members here are also guys from the job site...lolI know that, we are getting off base. I feel like I am on a job site. My question is the first Post.
| (Southwire Cable Tech Support) Sep 27, 2021, 2:58 PM EDT Allan, In my experience, mobile home services are comprised of utility service conductors connected to a power pole (main power disconnect) and then through a feeder from the pole to the mobile home. This feeder requires an EGC and is normally installed underground. Bare conductors are not allowed in underground installations, even for the EGC. If the feeder is installed above ground, there may be concern for a higher probability of mechanical damage to the feeder going into a mobile home (versus other kinds of buildings). FYI, here is the response from Southwire. It makes sense to me, and is in line with what was said by you guys. I would like to thank you all for your input, I read your reports all the time and it helps me. |