Re: mobile home service question
Here is what I posted in another thread As far as needing a raceway:
quote:
--------------------------------------------------------------------------------
24 CFR Part 3280
3280.803
Power supply.
(2) An approved raceway from the disconnecting means in the
manufactured home to the underside of the manufactured home with
provisions for the attachment of a suitable junction box or fitting to
the raceway on the underside of the manufactured home. The manufacturer
shall provide in his written installation instructions, the proper
feeder conductor sizes for the raceway and the size of the junction box
to be used;
3280.808
Wiring methods and materials.
(k) When outdoor or under-chassis line-voltage wiring is exposed to
moisture or physical damage, it shall be protected by rigid metal
conduit. The conductors shall be suitable for wet locations. Electrical
metallic tubing may be used when closely routed against frames, and
equipment enclosures.
(l) The cables or conductors shall be Type NMC, TW, or equivalent.
--------------------------------------------------------------------------------
This is out of 24 CFR of the HUD codes that apply to manufactured homes. and it overrides State and local codes
The hud inspector here will allow it if there is a conduit from the required disconect within 30' of the trailer to the underside of the of the trailer. But I not sure what he is using to allow it? as 24 CFR 3280.808 clearly requires conduit.
And I'm not sure what you mean as a permanant foundation as you stated it also has skirting? As how can it have both? at least to HUD codes what a permanant foundation is.