I’m looking at a potential job to install a generator for a mobile home. Problem is, it’s a mobile home (hitch and axles still attached) originally it was cord and plugged with a 40A 125/250V rating (still placarded on the trailer). At some point someone removed the cord and ran a underground 60A feed in PVC from the panel (60A Main/Range) to a pole outside on the property with a meter socket and no disconnect.
Also, the panel is located in a clothes closet in the bedroom.
What kind of issues do you think if any? If I was to relocate the panel outside the closet with a new 16 or 20 circuit panel (less than 3' from it's current location) with a 50A main and install a new 4-wire cord as a feeder with a 50A 125/250V plug in accordance with Article 550 to be connected to a 50A 125/250V Meter/disconnect/receptacle combination enclosure on the pole.
Thinking if I bring the trailer back to its somewhat original state, then I can install a generator without all the violations. Only concern I have is if I do this, do you think there would be any issues with it no longer being UL listed? especially from a liability stand point.
Thanks
Also, the panel is located in a clothes closet in the bedroom.
What kind of issues do you think if any? If I was to relocate the panel outside the closet with a new 16 or 20 circuit panel (less than 3' from it's current location) with a 50A main and install a new 4-wire cord as a feeder with a 50A 125/250V plug in accordance with Article 550 to be connected to a 50A 125/250V Meter/disconnect/receptacle combination enclosure on the pole.
Thinking if I bring the trailer back to its somewhat original state, then I can install a generator without all the violations. Only concern I have is if I do this, do you think there would be any issues with it no longer being UL listed? especially from a liability stand point.
Thanks