I've been going through the mike holt exam prep 2002 book and have come across 2 similar questions on mobile homes with an answer that I'm not sure is correct.

The question is:

The power supply to the mobile home shall be ____

A. One 50A mobile home power-supply cord with attachment plug
B. Permanently installed feeder
C. A or B
D. None of these

I chose C because art. 550.10 says the power supply to the mobile home shall be a feeder assembly consisting of not more than one listed 50-ampere mobile home power-supply cord with an integrally molded or securely attached plug cap or a permanently installed feeder.

Now there were 2 questions basically the same as this and The answer it always gives is A, just the Cord assembly. Is there another section I'm missing or is this just an error in the book that's been missed a few times?