A arnettda Senior Member Oct 5, 2009 #1 Am I on the right track. 550.10 power supply for a mobile home. If I run #2 al into the panel from a disconect located outside would this be acceptable as a permanetly installed feeder? It also needs to be a 4 wire feeder?
Am I on the right track. 550.10 power supply for a mobile home. If I run #2 al into the panel from a disconect located outside would this be acceptable as a permanetly installed feeder? It also needs to be a 4 wire feeder?
R RUWired Senior Member Location Pa. Oct 5, 2009 #2 If the indoor panel is rated at 100 amps and the # 2 is in a raceway or cable, article 550.33(B) allows it. Yes 4 insulated conductors are required. Rick
If the indoor panel is rated at 100 amps and the # 2 is in a raceway or cable, article 550.33(B) allows it. Yes 4 insulated conductors are required. Rick