I have a mech equipment with MOCP 15Amp. If I use a 20 Amp breaker, is that a code violation?
or should I install a 15Amp fused disconnect switch at the equipment fed from a 20amp breaker in the panel board?
There shouldn't be a starting issue. The OP says the MOCP (maximum overcurrent protection) is 15 amps.It may or may not start, if not, the NEC doesn't care, as long as it's safe. You can put a 20A breaker on the HV side of a transformer rated for 1000A. You won't get more than 20A out of it, but NEC doesn't care as long as the 20A circuit install meets NEC.
What will happen if mechanical internal wiring rated for 15A (16awg) and you put 20 or 25 branch circuit? NEC doesn't care about this situation? How much bigger you can but branch circuit?
Sent from my Nexus 5 using Tapatalk