The MOCP on the WSHP (equipment) nameplate is 10 Amps @ 480 volts, single phase. There is an exception for Individual Motor Compressor under 440.22 (A): The rating of the branch-circuit short-circuit and ground-fault protective device shall not be required to be less than 15 amperes.
Equipment falls under 440.22 (B) Rating or Setting for Equipment since it has a pump and UV light. There is also the section 440.22 (C).
I want to use a 15 amp CB to feed the WSHP. The WSHP has a factory mounted UFDS. Would the Exception still apply?
Equipment falls under 440.22 (B) Rating or Setting for Equipment since it has a pump and UV light. There is also the section 440.22 (C).
I want to use a 15 amp CB to feed the WSHP. The WSHP has a factory mounted UFDS. Would the Exception still apply?