Good Morning Everyone,
Long time reader of the forum, first post.
TLDR: What part of the code requires that manufacturer nameplate MOCP be adhered to?
---
I'm trying to find out if/which section of code requires that the MOCP for an HVAC unit must be adhered to.
Here's why:
I'm working on a project and got the equipment schedule from the mechanical guys. MOCP of 15A on two units. No problem, they make 15A two pole 208 breakers commonly. So that's what I put on the panel schedule.
Markups from PE come back and one of his comments is "20 Amp minimum on commercial projects". I send back a new set but I mark this up as "15 Amp MOCP per mechanical". I get the next drawing set back and it says "20 Amps is the minimum we use on commercial projects. Never use 15 amps. Change it".
At this point I'm floored. Just "change it"? No mention of a fused disconnect or anything like that. So I change it and send it back. But everything I've been taught up to this point is that MOCP on a nameplate is because the conductors inside the device are sized such that you need to use a maximum size breaker. And we just busted that.
I've been looking through 100, 300, and 400 but I can't seem to find anything along the line of "thou shalt follow the nameplate" or "MOCP or die". Anyone know what part of the code might require the nameplate MOCP to be followed?
Long time reader of the forum, first post.
TLDR: What part of the code requires that manufacturer nameplate MOCP be adhered to?
---
I'm trying to find out if/which section of code requires that the MOCP for an HVAC unit must be adhered to.
Here's why:
I'm working on a project and got the equipment schedule from the mechanical guys. MOCP of 15A on two units. No problem, they make 15A two pole 208 breakers commonly. So that's what I put on the panel schedule.
Markups from PE come back and one of his comments is "20 Amp minimum on commercial projects". I send back a new set but I mark this up as "15 Amp MOCP per mechanical". I get the next drawing set back and it says "20 Amps is the minimum we use on commercial projects. Never use 15 amps. Change it".
At this point I'm floored. Just "change it"? No mention of a fused disconnect or anything like that. So I change it and send it back. But everything I've been taught up to this point is that MOCP on a nameplate is because the conductors inside the device are sized such that you need to use a maximum size breaker. And we just busted that.
I've been looking through 100, 300, and 400 but I can't seem to find anything along the line of "thou shalt follow the nameplate" or "MOCP or die". Anyone know what part of the code might require the nameplate MOCP to be followed?