Have a failed inspection because the inspector claims that the MOCP is the only size allowed. There is no Min breaker size listed on data plate but the breaker we installed is over the MCA but less than the max OCP. When I said ok we will put a 60 amp breaker on the #8 wire and he said no way the wire is not rated for 60 amps. I found in one of the newsletters good info about the fact you can put a breaker that is rated higher than the wire (as long as it is no more than the MOCP) but can not find in plain English anything that states the OCP can be smaller than the rated MOCP. Even sent him the below article by Micheal Johnston from the NECA but he says no go. Any other sources out there that any one knows of.