Can we use 20A breaker instead of 15A breaker (either single phase or 3-phase cases) to protect an equipment with MOCP=15A shown on its data sheet?
Can we use 20A breaker instead of 15A breaker (either single phase or 3-phase cases) to protect an equipment with MOCP=15A shown on its data sheet?
it would not be code compliant if it was the only OCPD.
Another scenario...If the data sheet does not have MOCP value, can we use 20A CB if this is a heater and running load is 7.2A?
what kind of heater is it?
for example, 424.22 has overcurrent protection requirements for electric space heaters.
each of the articles that applies to different types of electric heaters has different requirements for the OCPD.
Unless there are other mitigating factors not mentioned, I say yes, it is permitted. Requirements are covered in 210.22 or 210.23(A). You have to remember that OCPD rating is basically to protect the circuit conductors, not the supplied equipment.wall mounted electric heater.
Unless there are other mitigating factors not mentioned, I say yes, it is permitted. Requirements are covered in 210.22 or 210.23(A). You have to remember that OCPD rating is basically to protect the circuit conductors, not the supplied equipment.
MOCP=15A shown on its data sheet?
I concede to your comment over mine...I am sticking with no assuming the 'data sheet' matches the units labeling.