More info on the problem
More info on the problem
Full disclosure - I am working with Mr. 55 Classic Ride on this project.
Charlie B - I understand your issue of the panel being used in accordance with manufacturer's instructions. However, this installation is in an electrical generating station owned by the utility. As such, it is not under the auspices of the NEC. What I need is some engineering analysis of this installation.
In our design, we are replacing a three-phase inverter with a single phase unit. Apparently, there were once some 208 Volt three-phase loads fed from this inverter, but not any more. Since all loads are now single phase, we wish to replace the inverter with a single-phase unit. The sticking point is that these loads feed a number of computer systems throughout the plant. Operations is very concerned about how long these systems will be out of service during the installation of the new inverter. Of course, replacing the panels will lengthen the time that these systems are out of service, and makes the problem worse. We will have a temporary feed to supply these loads during construction, but this is still seen as a higher-risk power supply than a battery-backed inverter. In other words, during the time of construction, there will be ahigher risk of losing these loads due to a power supply failure than if the inverter were in service. This is where the push is coming from for re-using these three phase panelboards in a single phase application.
When this idea was first presented to me, I thought it was silly, and probably dangerous. After looking at it, I'm starting to agree with the utility that it is a workable solution. We were already going to add a warning placard to alert personnel that the panel has been converted to single phase, very similar to the one that Don_Resqcapt19 pointed out in his post.
Here are the key points - 1) the panel voltage will be within manufacturer's ratings (120 Volt single phase), 2) the inverter limits fault current to a value well within the panel short circuit rating, and 3) no modifications are being done to the panel internals. The plan is to utilize the existing 4 wire power conductors to supply the panel. The major difference is that these three conductors are now carrying 120 Volt power that is in phase with each other instead of being 120 degrees out. Line-to-line voltage is now zero.
Can you come up with any reasons why this would be a bad idea? If there is a solid engineering reason for not doing this, we will dig our heels in and tell the utility "no". However, after spending some time thinking about it, I'm not finding any reason why it won't work. Anybody have any thoughts?