Modification to Load Side Bus Bar

Status
Not open for further replies.

MEP Guy

Member
Is it permissible to remove a section of bolted bus bar on the load side of a main circuit breaker (1200A) ? This would be done to allow tapping of each open end to allow it to be wired through an automatic transfer switch.

I suppose it is a UL issue, but if permitted by the AHJ...? Any specific code violations ?

Thanks for any help.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Pierre C Belarge said:
. If they permit this, I would ask for it in writing to present to the AHJ and keep a copy for your records.

which, from my experience in asking mfgs. for such, is that you have as much chance getting a letter as you do finding a snowball in he**

understanderbly(?), they don't want the liability.
 